Best Practices – Holden – Combined Cycle Journal

Best Practices – Holden

Award control system mods enable 10-min starts; increase reliability, flexibility

Best Practices Award

 

Challenge. The primary business challenge motivating Holden Power Plant’s Fast Start Project was the transition from 300 MW of wind at the beginning of 2012 to 600 MW of wind at the beginning of 2013, with another 150 MW under contract for the future. This addition of wind requires increased flexibility of other assets to address the variable power supply of the renewable resource.

Solution. AECI hired Siemens Energy Inc to modify startup logic and controls, as well as to re-tune to improve the full-load start time. Details of the logic changes and implementation follow:

• Modified logic for the air dampers and fuel-gas isolation valve to allow them to open earlier in the startup sequence.

• Modified logic for the fuel-gas isolation valve to allow proper opening and closing in the event of a trip on startup.

• Modified logic for the ignition gas valves to allow optimized operation.

• Modified logic to allow the operator to select fast or normal start.

• Added logic to allow the fast-start load gradient to be operator-selectable from 10 to 27 MW. The original load gradient was 10 MW/min; fast start uses the 27-MW/min loading.

• Modified logic to allow fast-start selection through the RTU interface.

• Modified IGV logic to allow successful premix operation through the faster transfer time.

• Modified pilot-gas-valve logic to enhance flame stability.

• Fast-start load gradient kicks out once the load set point is reached or when outlet temperature control (OTC) is achieved.

• Adjusted startup parameters to make the startup curve more linear from 150 to 3600 rpm.

Results. Before the fast-start modification, the Holden units were AECI’s fastest starting units at 15 minutes from beginning of start to full load. Full-load start time was reduced by an average of 6 minutes to an approximate 9-min full-load start time. More specifically:

Unit 11: 8 min 59 sec (6 min 17 sec improvement).

Unit 12: 8 min 51 sec (5 min 3 sec improvement). See Figs 1, 2.

Unit 13: 9 min 19 sec (6 min 45 sec improvement).


• The Fast Start Project began Sept 26, 2012 and was completed on October 5. It was a team effort among OEM Siemens, Holden personnel, and Associated Electric Cooperative Inc’s headquarters engineering staff.
Key project highlights/facts included the following:

• Base load for fast-start testing was 103 MW; normal ramp rate was 10 MW/min, fast-start rate 27 MW/min. The ramp rate is selectable by system operators via the RTU interface.

• The fast-ramp rate applies only to fuel-gas starts; ramp rate on fuel oil remains unchanged at 10 MW/min.

• Faster start times were achieved only through logic and tuning changes. There were no physical modifications to the equipment.

•The first fast start was called for less than 24 hours after project completion; expectations were met.

• From commissioning in October 2012 through January 2013 there were a total of 22 fast starts on the three units arranged for that capability; all were successful. There also were 25 normal starts.

• Late last January, all three units were called on to fast-start concurrently following the trip of a coal-fired unit. Expectations were met.

Disturbance control standards. Faster Holden starts allow AECI to better comply with NERC Standards for DCS events. BAL-002 requires the utility to provide reserves within 15 minutes following a DCS event. Holden often is counted as AECI’s non-spinning contingency reserves. A faster start time allows for better compliance with this standard.

Control performance standards. Faster Holden starts provide better compliance with BAL-001 CPS. A newly proposed revision of BAL-001 and a field trial, in which AECI is participating, requires correction of negative Area Control Error (ACE, under generation) within 30 minutes during periods of low frequency. A faster Holden start time allows for other options to be exercised first to try to mitigate a BAAL (Balancing Authority ACE Limit) event. This allows for more time before Holden units have to be started, actually reducing the number of Holden starts and keeping costs low.

Renewables integration. Faster Holden starts give AECI more megawatts faster helping it mitigate the risks with wind. With more wind generation coming on line, the utility had to address the system responsiveness. Several alternatives were considered on the basis of cost—from constructing new units to modifying other units to start in less than 10 minutes. The economic solution was arranging for fast-start capability at Holden.

Participants:

Joel Wilhite, senior CT specialist

David Shirley, senior CT specialist

Rod Rupert, controls engineer

Steve Combs, controls engineer

Mark Treat, principal engineer